I'm trying to figure out what wire gauge/conductor quantity I need to run from my 200amp meter main to the service panel in my house. Anybody work in the field of residential electrical? The wiring will be buried underground.
 
We sell all kinds of other stuff in our Etsy store!
OP
Brodiesel710

Brodiesel710

Burrito fund contributor
StP Supporter
Top Poster of the Month
Joined
Mar 5, 2019
Messages
965
Location
Winnemucca
Website
www.ebay.com

Faceplant

Mmmm . . . Taste the Ballast!
Joined
Nov 29, 2018
Messages
401
Location
Boulder Creek Ca
2/0 copper, 4/0 aluminum. I would not use aluminum, if I were you, and I would not run direct burial cable.

Home Depot used to have a nice booklet called “ Code Check Electrical”, showing the most recent code cycle requirements. If you cannot get it there, I bet Amazon or eBay will have it.

It has excellent drawings showing service entrance requirements for conductor sizing, grounding and bonding guidelines, conduit sizing, ground rod sizing, and lots more considerations.

Stop at a local residential jobsite around lunch , preferably on a Friday, with a cooler of ice cold beer. I’ll bet one of those guys will come to your house after work and show you just how to do it. Do not take advice from workers at Home Depot, I heard more wrong info being dispensed there than I can shake a stick at.
 
OP
Brodiesel710

Brodiesel710

Burrito fund contributor
StP Supporter
Top Poster of the Month
Joined
Mar 5, 2019
Messages
965
Location
Winnemucca
Website
www.ebay.com
2/0 copper, 4/0 aluminum. I would not use aluminum, if I were you, and I would not run direct burial cable.

Home Depot used to have a nice booklet called “ Code Check Electrical”, showing the most recent code cycle requirements. If you cannot get it there, I bet Amazon or eBay will have it.

It has excellent drawings showing service entrance requirements for conductor sizing, grounding and bonding guidelines, conduit sizing, ground rod sizing, and lots more considerations.

Stop at a local residential jobsite around lunch , preferably on a Friday, with a cooler of ice cold beer. I’ll bet one of those guys will come to your house after work and show you just how to do it. Do not take advice from workers at Home Depot, I heard more wrong info being dispensed there than I can shake a stick at.
Yeah your like the 3rd guy to tell me not to use aluminum, I had 4/0 Alum. priced out, I will do copper. I was also on the fence about direct burial, popular around these parts for shorts runs to trailer homes but it didn't seem right, for how much length I need. Thank you @Faceplant!
 

Jackthereaper

Vagabond
Joined
Oct 5, 2018
Messages
286
Location
Earth
The answer to your question is yes. You will be pulling some 3/0 guage for a 200 amp service (you growing?). The neutral / ground bus is typically grounded at the meter can or in the panel for older installs(house ground which is typically brought in with the service but separate) as well as @ the last step down transformer on the pole (the neutral/ground coming from the service is sourced here)

bed06939-03c1-4230-860b-f8f5ca7e79fa-jpeg.53045

neutral/ ground wires in my panel w. labelled source .this is an old house, and the single ground rod is wired directly into the panel instead of the meter box which i believe would not meet code any longer where its installed

7C29EFA3-4196-4985-80B2-D20E54BDF40B.jpeg
Bare conductor is your service ground

0349171e-8781-406b-920f-09548a8c70d7-jpeg.53047

This is a nice drawing to sum it all up. Svc ground and ground rod both attached to neutral/ground bus in the main cabinet.(note the right panel has separate neutral and grounding busses but they all go to the same place). Don’t skimp on wire here, you need all 4. Your panel ground should never carry current, your neutral should handle all of it.

Do you have safety gear? These gloves are only $30 and protect you up to 17000 volts. Worth every penny imo
76aec786-caea-4feb-be9e-a6ce1c60613c-jpeg.53048
 
Last edited:
OP
Brodiesel710

Brodiesel710

Burrito fund contributor
StP Supporter
Top Poster of the Month
Joined
Mar 5, 2019
Messages
965
Location
Winnemucca
Website
www.ebay.com
The answer to your question is yes. You will be pulling some 3/0 guage for a 200 amp service (you growing?). The neutral / ground bus is typically grounded at the meter can or in the panel for older installs(house ground which is typically brought in with the service but separate) as well as @ the last step down transformer on the pole (the neutral/ground coming from the service is sourced here)

View attachment 53045
neutral/ ground wires in my panel w. labelled source .this is an old house, and the single ground rod is wired directly into the panel instead of the meter box which i believe would not meet code any longer where its installed

View attachment 53046
Bare conductor is your service ground

View attachment 53047
This is a nice drawing to sum it all up. Svc ground and ground rod both attached to neutral/ground bus in the main cabinet.(note the right panel has separate neutral and grounding busses but they all go to the same place). Don’t skimp on wire here, you need all 4. Your panel ground should never carry current, your neutral should handle all of it.

Do you have safety gear? These gloves are only $30 and protect you up to 17000 volts. Worth every penny imo
View attachment 53048
Sick! No I'm not growing, not yet anyways! haha, I'm building a house. And am distributing power to all new construction, well, house, and pole barn.

I'm going to dig in a little more to what you wrote, I may ask you some more questions. I have a lot of experience doing electrical but nothing "professional" or legit on the job, just figuring out my own projects.
 

Jackthereaper

Vagabond
Joined
Oct 5, 2018
Messages
286
Location
Earth
@Jackthereaper do you think this a good choice for a 300' run from my 200A meter to my house panel? It will be inside of Sch 40 PVC, underground.

http://platt.com/p/452102
For my money i would be running bigger aluminum for such a long connection. The 00 wire in the link is really only rated for 175 amps and your distance is quite long, i wouldnt risk it. I would be running 250-250-250-3/0 aluminum wire. 300 ft of 000-000-000-00 Copper to handle 200 amps is gonna be well over 4 grand , the aluminum will come in right around the thousand

Copper

Aluminum

Either way, eat your wheaties that morning. Shits gonna be heavy and hard as fuck to bend and pull through condiut. Using the 53% rule for one wire you will need some fat conduit as well. Measure the cavle, calculate its cross sectional area and then divide by .53 and round up to the next size conduit available.

Other than that its just gonna be full tilt like a peterbuilt and get it done. You have quite a project cut out
 
Last edited:

Jackthereaper

Vagabond
Joined
Oct 5, 2018
Messages
286
Location
Earth
When you use aluminum make sure to use some of this schmoo on the connections to any copper

When you are pulling real wire, copper just isnt an economical option. You will be fine with aluminum service cable.
 
OP
Brodiesel710

Brodiesel710

Burrito fund contributor
StP Supporter
Top Poster of the Month
Joined
Mar 5, 2019
Messages
965
Location
Winnemucca
Website
www.ebay.com
For my money i would be running bigger aluminum for such a long connection. The 00 wire in the link is really only rated for 175 amps and your distance is quite long, i wouldnt risk it. I would be running 250-250-250-3/0 aluminum wire. 300 ft of 000-000-000-00 Copper to handle 200 amps is gonna be well over 4 grand , the aluminum will come in right around the thousand

Copper

Aluminum

Either way, eat your wheaties that morning. Shits gonna be heavy and hard as fuck to bend and pull through condiut. Using the 53% rule for one wire you will need some fat conduit as well. Measure the cavle, calculate its cross sectional area and then divide by .53 and round up to the next size conduit available.

Other than that its just gonna be full tilt like a peterbuilt and get it done. You have quite a project cut out
Thank you so much, yeah when Platt shopping cart says "call for price" you know its expensive. I found that Southwire has really nice conduit fill and voltage drop calculators, so with that and your advice I'm golden. Full tilt, the only way to live.
 
OP
Brodiesel710

Brodiesel710

Burrito fund contributor
StP Supporter
Top Poster of the Month
Joined
Mar 5, 2019
Messages
965
Location
Winnemucca
Website
www.ebay.com
The answer to your question is yes. You will be pulling some 3/0 guage for a 200 amp service (you growing?). The neutral / ground bus is typically grounded at the meter can or in the panel for older installs(house ground which is typically brought in with the service but separate) as well as @ the last step down transformer on the pole (the neutral/ground coming from the service is sourced here)

View attachment 53045
neutral/ ground wires in my panel w. labelled source .this is an old house, and the single ground rod is wired directly into the panel instead of the meter box which i believe would not meet code any longer where its installed

View attachment 53046
Bare conductor is your service ground

View attachment 53047
This is a nice drawing to sum it all up. Svc ground and ground rod both attached to neutral/ground bus in the main cabinet.(note the right panel has separate neutral and grounding busses but they all go to the same place). Don’t skimp on wire here, you need all 4. Your panel ground should never carry current, your neutral should handle all of it.

Do you have safety gear? These gloves are only $30 and protect you up to 17000 volts. Worth every penny imo
View attachment 53048
Ok @Jackthereaper , kind of freakin' out here because I'm second guessing a lot of work I did.

First off my meter main (EATON) has a 200A service disconnect, will this trip at 200 AMPS or is it only a manual disconnect switch? The reason I ask is because my service entrance wires from here are going directly to my house 200A panel. THEN from the meter main I have another 90A breaker which is then powering my pole barn. Is this just a couple parallel circuits that could in theory over current the main?
 
OP
Brodiesel710

Brodiesel710

Burrito fund contributor
StP Supporter
Top Poster of the Month
Joined
Mar 5, 2019
Messages
965
Location
Winnemucca
Website
www.ebay.com
It sounds like your concerns are warranted. Can you please draw up the situation? English was my worst subject of study.

Never drew anything out officially but I figured out what would work for me, especially with your help.

Tell me this. I've laid 400' of 3" conduit with about 180 degrees of bend total, you think I could pull one run of 1/0 - 1/0 - 1/0 - 2 COPPER entrance cable or will there be hang ups?
 

Jackthereaper

Vagabond
Joined
Oct 5, 2018
Messages
286
Location
Earth
you will def want some wire lubricant for thay pull. Do you have a good strong rope laid into the conduit? Pull another with the wire so you can pull more later if necessary.

Never drew anything out officially but I figured out what would work for me, especially with your help.

Tell me this. I've laid 400' of 3" conduit with about 180 degrees of bend total, you think I could pull one run of 1/0 - 1/0 - 1/0 - 2 COPPER entrance cable or will there be hang ups?
[/QUOTE
 

Users Who Are Viewing This Thread (Users: 0, Guests: 1)

About us

  • Squat the Planet is the world's largest social network for misfit travelers. Join our community of do-it-yourself nomads and learn how to explore the world by any means necessary.

    More Info

Support StP!

Donations go towards paying our monthly server fees, adding new features to the website, and occasionally putting a burrito in Matt's mouth.

Total amount
$90.75
Goal
$100.00

Monthly Goals

  1. Paying the Bills
    $50.00 of $50.00 - reached!
    The first $50 in donations go towards paying our monthly server fees and adding new features to the website. Once this goal is reached, we'll see about feeding Matt that burrito.
  2. Buy Matt a Beer
    $75.00 of $75.00 - reached!
    Now that we have the bills paid for this month, let's give Matt a hearty thank you by buying him a drink for all the hard work he's done for StP. Hopefully his will help keep him from going insane after a long day of squishing website bugs.
  3. Feed Matt a Burrito
    $90.75 of $100.00
    Now that the bills are paid and Matt has a beer in his hand, how about showing him your love by rewarding all his hard work with a big fat burrito to put in his mouth. This will keep him alive while programming new features for the website.
  4. Finance the Shopping Cart
    $90.75 of $200.00
    Now that the bills are paid and Matt is fed, perhaps it's time to start planning for those twilight years under the bridge... if only he had that golden shopping cart all the oogles are bragging about these days.

Latest Status Updates

Anyone in Minneapolis at the protest, just got back here from Duluth
Anybody watching the SpaceX launch today?
Will do these posts occasionally so family and friends know we are alive and well.
Currently: in Mariposa, CA, getting ready to head to Coulterville, CA.
Always sucks to see good ppl/new friends get back on that ironhorse after getting to hangout/know, be safe friends an stay in touch! @Koala @scutellaria, maxy, Henry an well. Wish I was enroute South with y'all!
I hate my fucking back. A combination of bank bullshit and now a strained or sprained back had kept me held up in Pennsylvania. Have a place to stay, but I'm pissed at life trying to keep me off the road!
Fuck it, I'm getting a bottle
Wheat2020 wrote on Matt Derrick's profile.
I'mma cut to the chase: You don't call me what I consider to be a slur or insult, and I won't call you names.
You say I should love myself and have more self-confidence. You've got it all wrong. I love myself plenty, and I know for a fact that I am capable of doing incredible things, both good and evil.
You say fake it till you make it. I'm too honest for that. Instead I will have faith in myself, and act accordingly.
These new rules for the train riding forum are ridiculous. I've been on here for 5 ish years.
MFB wrote on Older Than Dirt's profile.
Just wanted to say you look waaay better in your new avatar pic. ;) You clean up nice!
Bent123 wrote on iamwhatiam's profile.
I read your story last month about working in Alaska. I got a job in Naknek this summer. Definitely can get how it felt like jail. I fear it's really going to feel that way with this virus. We can't go into town. I'm not very happy about that since it will limit my exploring. Yet I really need the opportunity right now. Anymore advice is much appreciated.

Members online

About us

  • Squat the Planet is the world's largest social network for misfit travelers. Join our community of do-it-yourself nomads and learn how to explore the world by any means necessary.

    More Info

Support StP!

Donations go towards paying our monthly server fees, adding new features to the website, and occasionally putting a burrito in Matt's mouth.

Total amount
$90.75
Goal
$100.00

Forum Statistics

Threads
25,560
Messages
235,733
Members
9,396
Threads in last 24 hours
11
Messages in last 24 hours
82
Members in last 30 days
877
Latest member
Ericaceae